Motor-thermal protection
Theff
North Carolina
Electrical Contractor
I’m trying to figure out if this motor is thermally protected. The manufacturer is saying it is thermally protected at 160°C. Everything I can find online is referencing the marking “Prot 160C” as the indication that it is in fact thermally protected. Internal to the motor and monitoring actual temperature rather than current. It’s a European motor and I thought maybe it’s the norm there or something. Is that correct? Any other people with experiences with this? Thanks
Pretty sure that’s the motors insulation class/thermal tolerance basically temps it can withstand overtime without damaging the motor , pretty sure thermal protection is usually marked “TP”
But its a European motor and “Prot 160c” could very well mean its thermal protection shuts it down when its operating temp hits 160c
I misspoke in my previous comment I didn’t not see the 155 for class F in the upper left hand corner of nameplate and after looking online just like you I’ve found that prot 160c should mean thermal protection but can’t verify
What we don't know is whether "prot 160c" means there is thermal protection in series with windings or if there is just thermostat leads that would need to be wired in series with the motor control circuit. With NEMA design motors those thermostat leads would usually be labeled "J", if it is an integral motor protector (on a NEMA motor) the protector leads usually are P1, P2... and so forth if there are more than two leads involved.
Good point
Unless the thermal protector is an on-board Kilxon, in which case there would usually be a red reset button on the bell housing.
Seen a fair amount of automatic reset types on small motors, some even buried in end housing of the motor so isn't even obvious it has such device until you disassemble the motor.
Good point.
While it is a NEMA convention to use the term “Thermally protected” or TP or something similar, I don’t know what the IEC terminology for that is, might be worth investigating.
PS: looks like this motor is not even following the IEC standards…
Link to article on IEC thermal protection markings
They apparently use “TP” followed by numbers to indicate the method.
Yeah I’ve seen motors with what you guys are describing. There isn’t any of those on this motor apparent to me, I haven’t disassembled the motor of course but I have inspected it thoroughly. In the motor connection box there are no thermostat leads or motor protection leads. Just standard power connection terminals. The manual for this motor states “A winding protection contact is integrated in all 1-phase motors at the factory to protect the motor against overheating.” But the nameplate is what is making me hesitate. This motor is an older model motor, but according to the manufacturer the manual (which is used with newly manufactured motors) is applicable to the older motors as well.
I would say since your motor has a FLA of 8 amps, it could be possible there is an integral thermal switch capable of interrupting that sort of current. Start going over 10 maybe 15 amps and it would more likely be a pilot duty type of thermostat intended to connect to a control circuit if embedded within motor windings and would have leads run to the termination box.