In a class 1 div 2 area we have an installed XP motor, does the code require the thermal switch be connected?
My understanding of 501.125, is that the thermals are required to prevent the enclosure temp from exceeding the T rating (which must be less than 80% of the AIT) of the motor and that is only required in a C1 D1 area when using a motor specified in A(2) or A(3).