We have a 100 Hp, 480 volt, 3 phase motor (124 Amps) 200 feet away from a VFD. To calculate the voltage drop should I use the 124 amp motor running current or the 155 (124 x 1.25) amp wire sizing amps? Moving the VFD closer is not an option - darn. Allowing for 10% loss in the drive, the total load is then 124 x 1.1 x 1.25 or 170 amps. Should the breaker be 200 amps or 225? Am I over thinking this? It appears that I am walking the fence. Thanks for your help and have a good day/night!