motor specs
motor specs
you would have to check with the motor specifications, most motors are rated to operate at +/- 10% voltage, so a 230V motor would operate normally up to 253V and down to 207V. With that being said It would not be a good idea (in my opinion) just because the minimum operating voltage of a 208V system could be as low as 187V. nominal 208V +/- 5% for voltage drop within the facility plus +/- 5% utility variations, so if you have a 208V system either use a motor rated for a 208V system or provide a buck/boost transformer depending on the size you could probally use two transformers connected in an open delta configuration to power a three phase only load, if you run the motor on a 208V system you could run into problems on utility and building voltage anomoniles. Just my 2 cents.