To my forum colleagues, I present my electrical dilemma, requesting your particular expertise....
I have a Well-pump building powered at 240V, 3 phase delta. The building is equipped with a VFD/Across-the-line starter combo feeding a 40 HP 480V motor.
... long silly story.. new construction... but what I'm told is that there is no 240V 40 HP deep well pump with the required characteristics, so we either change the service and starters, or .... and that's where I could use some of the forums experience...
My thought is to install a padmount transformer at the motor, 240:480 (3) phase delta/delta, sized at 3-5 times the motor size, or 150-225 kVA. I'll run an SKM Transient Motor Starting exercise, and get comfortable with the size.. for an across-the-line start.
But I'm uncomfortable with the VFD. My concern is the magnetization of the transformer/motor starting current, and how the VFD will respond to that.
I figured I'd call Square D, and ask them. But there are likely more experienced folks here than I'll get at 888 SQUARE D.
Any thoughts are appreciated, about the xfmr approach, or any other suggestions.
Thanks,
John M
I have a Well-pump building powered at 240V, 3 phase delta. The building is equipped with a VFD/Across-the-line starter combo feeding a 40 HP 480V motor.
... long silly story.. new construction... but what I'm told is that there is no 240V 40 HP deep well pump with the required characteristics, so we either change the service and starters, or .... and that's where I could use some of the forums experience...
My thought is to install a padmount transformer at the motor, 240:480 (3) phase delta/delta, sized at 3-5 times the motor size, or 150-225 kVA. I'll run an SKM Transient Motor Starting exercise, and get comfortable with the size.. for an across-the-line start.
But I'm uncomfortable with the VFD. My concern is the magnetization of the transformer/motor starting current, and how the VFD will respond to that.
I figured I'd call Square D, and ask them. But there are likely more experienced folks here than I'll get at 888 SQUARE D.
Any thoughts are appreciated, about the xfmr approach, or any other suggestions.
Thanks,
John M