Guys,
TX for all the posts.
This is a final update to my well pump motor voltage dilemma.. hopefully.
Square D is the manufacturer of the VFD that was bought for the job, and they said it would be okay to run the VFD through a xfmr to the motor, but the VFD would need to be sized 25% larger than the motor. Too late, VFD is bought...
It ends up that the City has a spare 480V, 50 HP VFD/bypass drive that we will likely use for the 40 HP well pump motor. The Electric Dept can mount 12470:480V service in short order.
.. game over..... we'll see