Re: Motor voltage?
Ok I may be wrong on allowing a 440 volt motor on a 480 volt system.
But, its clearly a violation to use a 200 volt (for 208) rated motor on a 240 volt system with utilization voltage for the motor of 230 v.
Motors are rated with a utilization voltage that is lower than the sytem voltage, 200 for 208, 230 for 240, to allow for voltage drop from the source.
What about 440? Hmmm, not sure, its a secondary voltage that went away a long time ago. 110 and 220 still exist at the big box stores, like this:
Homeowner: I need to install a 220 v plug for my welder.
Big box sales person: Sure you'll find the 220V plugs on aisle 6 right next to the 110 v outlets.
What I would be concerned with is the motor current does increase if the applied voltage is more than 10% above the motor rating. So a 440 V motor may ok in one location, but not another.