Can some one explain me about the name plate of this induction motor ? What is the difference between option 3 and 4. What if we connected it to 460 star connection?
You got me. And while it is probably just a bad plate, it looks like it is telling you that at 230 the motor draws 0.27 amps.
:slaphead:I believe that is the rating of the brake, not the motor itself.
Sent from my iPad using Tapatalk
It is more lightly loaded on option 4 and the slip is less.Hi
good morning.
Can some one explain me about the name plate of this induction motor ? What is the difference between option 3 and 4. What if we connected it to 460 star connection?
7.5 is rated
8.6 is at 1.15 SF
Yes. 746W per HPKind of on track with the last couple posts here, it is rated at 7.5kW for 50 Hz.
@ 60 Hz you get one set of current, power factor, speed, etc. data, but it apparently is also rated 8.6 kW with another set of current, power factor, speed, etc. This may simply be the NEMA motor equivalent to a service factor?
Add: or maybe gives the motor the same rating as a NEMA motor rated in HP instead of KW?
I agree, but because putting the term "Service Factor" on an IEC motor would cause confusion for IEC customers, they show it like this, knowing that IEC customers will ignore the 460/60 ratings anyway.
So in NEMA world, this is a 10HP motor with a 1.15 SF.
I hadn't thought about a 1.15 SF before Ing noted it.
But it made me wonder why the rating isn't expressed in HP at least for the 60Hz ratings.*
Also interesting that for both 50Hz and 60Hz, the continuous rating is given as 7.5kW.
* Because it's Siemens... "Zere is der right vay, und der wrong vay, und der Ziemens vay. Der right und der wrong ist unimportant, you VILL do it zees vay und you vill like it!"