Hi

good morning.
Can some one explain me about the name plate of this induction motor ? What is the difference between option 3 and 4. What if we connected it to 460 star connection?
 

Attachments

  • motor.jpg
    motor.jpg
    68.8 KB · Views: 2

Strathead

Senior Member
Location
Ocala, Florida, USA
Occupation
Electrician/Estimator/Project Manager/Superintendent
Hi

good morning.
Can some one explain me about the name plate of this induction motor ? What is the difference between option 3 and 4. What if we connected it to 460 star connection?

You got me. And while it is probably just a bad plate, it looks like it is telling you that at 230 the motor draws 0.27 amps.
 

retirede

Senior Member
Location
Illinois
I'll fancy a guess....First of all, the "-Z" at the end of the Siemens catalog number indicates some special construction. #4 is simply the numbers at 460/60 when the motor is loaded at nameplate power (7.5 KW), #3 is max load at 460/60. Connecting 460 in wye would only be suitable for starting using a wye-delta starter, probably not practical for continuous use. There is no 60 hz wye rating because the correct voltage would likely exceed the insulation design voltage.


Sent from my iPad using Tapatalk
 

Besoeker

Senior Member
Location
UK
Hi

good morning.
Can some one explain me about the name plate of this induction motor ? What is the difference between option 3 and 4. What if we connected it to 460 star connection?
It is more lightly loaded on option 4 and the slip is less.
 

Jraef

Moderator, OTD
Staff member
Location
San Francisco Bay Area, CA, USA
Occupation
Electrical Engineer
7.5 is rated
8.6 is at 1.15 SF

I agree, but because putting the term "Service Factor" on an IEC motor would cause confusion for IEC customers, they show it like this, knowing that IEC customers will ignore the 460/60 ratings anyway.

So in NEMA world, this is a 10HP motor with a 1.15 SF.

If connected in Star and applied with 480V your torque would drop to 1/3 of rated, so in essence you could use it as a 3HP motor with higher than normal slip and poorer power factor. Why would you want to do that unless as a Star-Delta starting scheme? I have no clue.
 
Last edited:

kwired

Electron manager
Location
NE Nebraska
Kind of on track with the last couple posts here, it is rated at 7.5kW for 50 Hz.

@ 60 Hz you get one set of current, power factor, speed, etc. data, but it apparently is also rated 8.6 kW with another set of current, power factor, speed, etc. This may simply be the NEMA motor equivalent to a service factor?

Add: or maybe gives the motor the same rating as a NEMA motor rated in HP instead of KW?
 

Jraef

Moderator, OTD
Staff member
Location
San Francisco Bay Area, CA, USA
Occupation
Electrical Engineer
Kind of on track with the last couple posts here, it is rated at 7.5kW for 50 Hz.

@ 60 Hz you get one set of current, power factor, speed, etc. data, but it apparently is also rated 8.6 kW with another set of current, power factor, speed, etc. This may simply be the NEMA motor equivalent to a service factor?

Add: or maybe gives the motor the same rating as a NEMA motor rated in HP instead of KW?
Yes. 746W per HP

7.5kW / .746 = aprox. 10HP

10HP x 1.15SF = 11.5HP

11.5HP x .746 = aprox. 8.6kW
 

Besoeker

Senior Member
Location
UK
I agree, but because putting the term "Service Factor" on an IEC motor would cause confusion for IEC customers, they show it like this, knowing that IEC customers will ignore the 460/60 ratings anyway.

So in NEMA world, this is a 10HP motor with a 1.15 SF.

I hadn't thought about a 1.15 SF before Ing noted it.
But it made me wonder why the rating isn't expressed in HP at least for the 60Hz ratings.
Also interesting that for both 50Hz and 60Hz, the continuous rating is given as 7.5kW.
 

Jraef

Moderator, OTD
Staff member
Location
San Francisco Bay Area, CA, USA
Occupation
Electrical Engineer
I hadn't thought about a 1.15 SF before Ing noted it.
But it made me wonder why the rating isn't expressed in HP at least for the 60Hz ratings.*
Also interesting that for both 50Hz and 60Hz, the continuous rating is given as 7.5kW.

* Because it's Siemens.... When I worked there, we had an internal quip about "why" questions (said with an exaggerated German accent).

"Zere is der right vay, und der wrong vay, und der Ziemens vay.
Der right und der wrong ist unimportant, you VILL do it zees vay und you vill like it!"
 

Phil Corso

Senior Member
* Because it's Siemens... "Zere is der right vay, und der wrong vay, und der Ziemens vay. Der right und der wrong ist unimportant, you VILL do it zees vay und you vill like it!"

So you too, have been influenced by "Herr Doctor"... the man in a white lab-coat, w/ glasses, a clip-board, and 6 colored pens in a pocket-protector! ! !

Phil
 