I need to have a panel built for a 480V part of a job. Before I do I just wanted to check to make sure I have them put in the correct breakers. There are two motor controllers that will need to be fed by this panel. The customer bought this equipment used.
The first has a 25 hp with a FLA on the nameplate of 30 amps. The code book says the FLC is 34 amps at 460V. Currently the motor has #10's feeding it but would I be required to put in #8's to accommodate 125% of the FLC? Also, 250% of the FLC is 85 amps. Would I be allowed to us a 90A breaker?
The other motor controller feeds a 5 hp 460V motor. The FLA on the nameplate is 6.5 and the code book says the FLC is 7.6A. 7.6A x 125% is 9.5A. I should be fine to use #12's easily enough and fuse it with a 20A breaker --- 250% of 7.6 = 19A.....right?
I want to be very sure that I build the panel with the correct breakers since it's pretty costly.
Thank you.
The first has a 25 hp with a FLA on the nameplate of 30 amps. The code book says the FLC is 34 amps at 460V. Currently the motor has #10's feeding it but would I be required to put in #8's to accommodate 125% of the FLC? Also, 250% of the FLC is 85 amps. Would I be allowed to us a 90A breaker?
The other motor controller feeds a 5 hp 460V motor. The FLA on the nameplate is 6.5 and the code book says the FLC is 7.6A. 7.6A x 125% is 9.5A. I should be fine to use #12's easily enough and fuse it with a 20A breaker --- 250% of 7.6 = 19A.....right?
I want to be very sure that I build the panel with the correct breakers since it's pretty costly.
Thank you.