Jpflex
Electrician big leagues
- Victorville
- Electrician commercial and residential
I’m installing a 3 phase 480 Volt, 5 HP motor
To determine SOOW cord wire size input to the motor:
I determined the FLA for the motor is 7.6 amperes according to NEC table 430.250
I then took 1.25 percent x 7.6 amperes to ensure the selected SOOW cord would be sized proper
= size wire capable of 9.5 amperes
NEC table 400.5 (A) 1 indicates selecting a 16 AWG or higher SOOW cord
However, I do not see any tables for ampere ambient temperature adjustment as you would with THHN. Conductors are not more than 3. Are you required to adjust ampacity for ambient temperature for cord? Our location has a design temp of 100 degrees free height according to copper.org
Normally I would derate THHN ampacity with starting insulation temperature rating of 90 degrees celcius to 0.91 percent for this ambient temp correction. However, I don’t know how this is to be done with jackets SOOW cord?
NOTOR DISCONNECT: 430.109
Lastly I’m trying to figure out a proper sized disconnect within 50 ft of motor
At company scrap piles, I found a disconnect rated at 575 volts which is overkill to applied 480v, 15 hp rated with fuses at 30 amperes (motor controller VFD overcurrent protection and overload already supplied upstream and selected by engineer previously)
I am not sure how to select disconnect interrupting current or if I need to know motor locked current with FLC? Do I need to verify this on selection? Thanks