I have (6)3 phase motors that I need to connect and am hoping someone will check my math.
Coming out of a panel with 2 circuits in 1" PVC conduit before branching off to feed 3 motors in both direction.
Circuit 1. (3) 5 hp motors.
Feeder Conductors. 16.7 FLC each so 125% of biggest+sum of others =54.275.
#6 THHN good for 65 amps(conductor bundling reduces to 60 amps-#6 still good).
Feeder Circuit Protection 250% of largest+sum of others=75.15 next size down=70
Circuit 2. (2)5 hp,and (1)3 hp motor.
Feeder Conductors.16.7,16.7, and 10.6 FLC. 125% of largest+sum of others=48.175.
#8 THHN good for 50 amps(conductor bundling reduces to 44 amps-need to increase to #6).
Feeder Circuit Protection 250% of largest+sum of others=69.05 next size down=60.
Branch Circuits for Motors.
#12 taps and branch conductors 5 hp motors with 50 amp breaker.
#14 for 3 hp with 30 amp breaker.
# 8 EGC from feeder panel.
Coming out of a panel with 2 circuits in 1" PVC conduit before branching off to feed 3 motors in both direction.
Circuit 1. (3) 5 hp motors.
Feeder Conductors. 16.7 FLC each so 125% of biggest+sum of others =54.275.
#6 THHN good for 65 amps(conductor bundling reduces to 60 amps-#6 still good).
Feeder Circuit Protection 250% of largest+sum of others=75.15 next size down=70
Circuit 2. (2)5 hp,and (1)3 hp motor.
Feeder Conductors.16.7,16.7, and 10.6 FLC. 125% of largest+sum of others=48.175.
#8 THHN good for 50 amps(conductor bundling reduces to 44 amps-need to increase to #6).
Feeder Circuit Protection 250% of largest+sum of others=69.05 next size down=60.
Branch Circuits for Motors.
#12 taps and branch conductors 5 hp motors with 50 amp breaker.
#14 for 3 hp with 30 amp breaker.
# 8 EGC from feeder panel.