Good Evening
I was hoping someone could help me with a motor question. I sent a motor out for repair and when it returned
the leads were different. The motor is a 200hp 480v 3 phase 60 htz. Continuous duty use. The name plate says 237 amps.
When it left the leads coming out of the motor were #6 parallel.
When it returned it the leads were single #4.
I looked up the manufacture of the leads and the chart for the wire says 190 amps for the #4.
My question is does the wire for the leads need to carry the FLC of the motor i.e. 237 amps ?
Or do motor manufactures and repair shops use a percentage of the FLC on the leads? Thanks