That is only a problem if you are installing service conductors not motors. You may have to dertae for conduit fill.

Not "may", you "have to" derate the conductor ampacity.

The reason I don't like this type installation is that we end up with live wires running parallel with conductors that have to be 'de-energized' in the case of LOTO. Should there be a contact between two wires of the same phase.......
 
Not "may", you "have to" derate the conductor ampacity.

The reason I don't like this type installation is that we end up with live wires running parallel with conductors that have to be 'de-energized' in the case of LOTO. Should there be a contact between two wires of the same phase.......
Any installation where conductors are installed in a raceway that is possible.
 