Need much more information on the application.
Distance from control points to VFD?
Volatile or non-volatile retention of the pot position?
Resolution of pot setting? For example 1024 positions.
Voltage across pot?
Load resistance on wiper?
Isolation voltage required between control point(s) and the VFD electronics?
Power available at VFD for circuitry? Like 5 V, +/-12 or 15.
Response time?
Will a D/A converter or equivalent work?
How are controlling points to operate? Pushbuttons or what?
Is power available at the controlling points?
How important is the remote capability? In other words how much money is available?
Are both control points to have equal priority of the control function?
.
Excuse me but I may have to go back to school for a few years to answer all of these.
distance to furthest 30'
position should be relatively stable
Simple 5k single turn. (What they use now.)
10v
Don't know
12v from VFD
Not critical
?
Pushbutton
We have 24v dc supply readily available
They can afford it, but lets say budget is $1000
They will be equal.
My best guesses anyway.
The VFD in question feeds product to another. They must be started while the operator is in the immediate area. Once up and running the operation is monitored in a relatively clean and quite location. They would like to be able to adjust the VFD from both areas.