SpotOn
Member
- Location
- Stamford CT
Hello, I am wiring an indoor pool in Connecticut. Believe it or not we are still on the 2005 nec until march 3rd 2014. The pool has aluminum windows with motorized windows. The motors are located 7' above the waterline and there is a 1 foot wide bluestone "path" between the pool and the windows. The inspector is treating the entire window as the motor and says we can't have them without a modification from the state. The windows are all bonded with #8 solid to the equipotential plane and the motors will be gfi protected. I can't find where it states I can't have these within 5 feet of the pool. I see680.21 680.22 but they pertain to window motors. What am I missing?