Have a current project where the client has two extruder systems. Both are used equipment and came from United States facilities.
One extruder drive motor (Siemens) is dual rated at:
315KW, 380/660V, 578/333A, 50 Hz, 1490 rpm
AND
353KW, 440V, 538A, 60HZ, 1780 rpm.
Voltage range is 360-400/630-690 at 50 Hz and 420-460V on 60Hz. FLA's are 549-610/318-349A at 50Hz and 515-564A at 60 Hz.
Never seen a dual Hz rated motor before!
Perhaps because the extruded motor is on a VFD?
The other extruder line has all 50Hz rated motors but all were supposedly run at 60Hz,
What gives?
The V/Hz for the 50Hz rating is 7.6, and at 60 Hz it's 7.333. I'm sure that the plant voltage originally was 460V (or even 480V) which puts the v/Hz at 7.6666.
So from a V/Hz standpoint, they are very close.
I thought that you can't / shouldn't run 50Hz motors on 60Hz, at least for FVNR motors. Motors on VFD's are different.. What did I miss?
Some of the motors are on VFS, and other are oil pumps, cooling fans, etc.
Am I making a mountain out of a mole hill?
One extruder drive motor (Siemens) is dual rated at:
315KW, 380/660V, 578/333A, 50 Hz, 1490 rpm
AND
353KW, 440V, 538A, 60HZ, 1780 rpm.
Voltage range is 360-400/630-690 at 50 Hz and 420-460V on 60Hz. FLA's are 549-610/318-349A at 50Hz and 515-564A at 60 Hz.
Never seen a dual Hz rated motor before!
Perhaps because the extruded motor is on a VFD?
The other extruder line has all 50Hz rated motors but all were supposedly run at 60Hz,
What gives?
The V/Hz for the 50Hz rating is 7.6, and at 60 Hz it's 7.333. I'm sure that the plant voltage originally was 460V (or even 480V) which puts the v/Hz at 7.6666.
So from a V/Hz standpoint, they are very close.
I thought that you can't / shouldn't run 50Hz motors on 60Hz, at least for FVNR motors. Motors on VFD's are different.. What did I miss?
Some of the motors are on VFS, and other are oil pumps, cooling fans, etc.
Am I making a mountain out of a mole hill?