motors, NEC design
lutron
Pennsylvania
Hey Guys,
Please second guess my design.
12 fan motors (direct drive) all 460 volts 1.5 HP
1. 430.150 says 3.0 amps ,when I get my hands on the motors if 430.6 (A) (1) exception no 3 applies I shall make proper changes.
2. 430.32 (A) (3) applies, No need for heaters.
3. 430.24 OK all the motors are the same so.... 3.0 x 1.25 = 3.75 + (11 x3.0) = 36.75. I shall use #8 thhn. for my branch circuit.
4. 430.28 (1) (2) (3) yes I will adhere to these rules. I shall use 12 gauge wire and 20 amp fuses for my 12 taps to the individual disconnects. A little oversized I know, but we stock tons of #12
5. 430.53 (c) (4) I will use a 40amp breaker in the panel.
I can't say enough good about this site. I thank all that take the time to help.
P.S I am an "inhouse" Electrician so there is no bidding to deal with. However if there is a more cost effective way of doing this I'm all ears.
Thanks again
Mike
Re: motors, NEC design
Duplicate. Closed.