Can someone help me to understand Table 430.22(E)?
For example: An intermittent duty freight elevator motor requires conductors rated at 140% of nameplate FLC for motors rated continuous duty. So -- if the continuous duty motor is run continuously, conductors must be rated 125% of table FLC. If, on the other hand, the continuous duty motor is run intermittently, conductors must be rated 140% of nameplate FLC.
It makes no sense!
If that is not confusing enough, a 5-minute rated motor running the same freight elevator shall be permitted to have conductors rated 85% of nameplate FLC
Any comments would be greatly appreciated
Brian Dolan
For example: An intermittent duty freight elevator motor requires conductors rated at 140% of nameplate FLC for motors rated continuous duty. So -- if the continuous duty motor is run continuously, conductors must be rated 125% of table FLC. If, on the other hand, the continuous duty motor is run intermittently, conductors must be rated 140% of nameplate FLC.