Hey Guys,
Please second guess my design.
12 fan motors (direct drive) all 460 volts 1.5 HP
1. 430.150 says 3.0 amps ,when I get my hands on the motors if 430.6 (A) (1) exception no 3 applies I shall make proper changes.
2. 430.32 (A) (3) applies, No need for heaters.
3. 430.24 OK all the motors are the same so.... 3.0 x 1.25 = 3.75 + (11 x3.0) = 36.75. I shall use #8 thhn. for my branch circuit.
4. 430.28 (1) (2) (3) yes I will adhere to these rules. I shall use 12 gauge wire and 20 amp fuses for my 12 taps to the individual disconnects. A little oversized I know, but we stock tons of #12
5. 430.53 (c) (4) I will use a 40amp breaker in the panel.
I can't say enough good about this site. I thank all that take the time to help.
P.S I am an "inhouse" Electrician so there is no bidding to deal with. However if there is a more cost effective way of doing this I'm all ears.
Thanks again
Mike
Please second guess my design.
12 fan motors (direct drive) all 460 volts 1.5 HP
1. 430.150 says 3.0 amps ,when I get my hands on the motors if 430.6 (A) (1) exception no 3 applies I shall make proper changes.
2. 430.32 (A) (3) applies, No need for heaters.
3. 430.24 OK all the motors are the same so.... 3.0 x 1.25 = 3.75 + (11 x3.0) = 36.75. I shall use #8 thhn. for my branch circuit.
4. 430.28 (1) (2) (3) yes I will adhere to these rules. I shall use 12 gauge wire and 20 amp fuses for my 12 taps to the individual disconnects. A little oversized I know, but we stock tons of #12
5. 430.53 (c) (4) I will use a 40amp breaker in the panel.
I can't say enough good about this site. I thank all that take the time to help.
P.S I am an "inhouse" Electrician so there is no bidding to deal with. However if there is a more cost effective way of doing this I'm all ears.
Thanks again
Mike