If you have a 20HP three phase motor that has a nameplate of 46A do you use table amps of 54A or nameplate amps in determining the overcurrent for the breaker.
46A x 250%= 115A go up to 125A
54A x 250%= 135A go up to 150A
Also when determing the disconnect size do you use table amps or nameplate
46A x 115%= 52.9A up to 60A
54A x 115%= 62.1A up to 100A
46A x 250%= 115A go up to 125A
54A x 250%= 135A go up to 150A
Also when determing the disconnect size do you use table amps or nameplate
46A x 115%= 52.9A up to 60A
54A x 115%= 62.1A up to 100A