dose101

Member
Is their a specific mounting height requirement for a 100A fused disconnect switch feeding the primary of a transformer?
 
A

a.wayne3@verizon.net

Guest
Re: Mounting heights for overload protection disconnect swit

Pierre,i have always wondered why a max. height is given but not a min. :confused: But for a mobile home it is 24 ins. min.even more :confused: Allen
 

iwire

Moderator
Staff member
Location
Massachusetts
Re: Mounting heights for overload protection disconnect swit

I agree with Websparky here, it depends on the location of the equipment being served.

404.8 Exception No. 2: Switches and circuit breakers installed adjacent to motors, appliances, or other equipment that they supply shall be permitted to be located higher than specified in the foregoing and to be accessible by portable means.
 