Is there any code reference in NEC
about concrete floor levels in electric rooms where MCC will be mounted?
I hear raise floor 2". Others say 4" concrete slab.
somebody know about it?
I believe he's referring to housekeeping pads . There is no code that says you have to have one. But if you do be sure to maintain workspace intrusions within guidelines and breaker height within maximums.
As far as workspace intrusions is concerned, do you make sure your equipment is exactly flush with the front of the housekeeping pad? The code probably dictates that it must be flush but we normally have a couple of inches sticking out of the front otherwise the anchor bolts don't catch very much meat. Technically a violation? Probably. Still safe?:happyyes:
(3) Height of Working Space. The work space shall be clear and extend from the grade, floor, or platform to the height required by 110.26(E). Within the height requirements of this section, other equipment that is associated with the electrical installation and is located above or below the electrical equipment shall be permitted to extend not more than 150 mm (6 in.) beyond the front of the electrical equipment.