msilva94
Member
- Location
- Allentown, PA, USA
- Occupation
- Electrical Engineer
As part of the design, the construction firm requested I mount the Panels feeding equipment overhead on the Mezzanine Walk-Through. This walk-thru is essentially an open grate platform with safety rails. Their concern is security and manageability, they do not want the panels easily accessible to the workforce (forklift damage, tampering, etc), but they still need to be located near the equipment/serviced areas.
I informed them that the panels require a minimum of 3' clearance in front for maintenance, would prefer it the path was closed (not open grate) and that I would need to confirm with the structural team whether the weight of the panels and associated conduit could be properly supported. In response, they’ve proposed widening the mezzanine to 4' and passed the concern along to the Structural Engineer.
As far as I understand and have read in the NEC (240.24), as long as the Electrical Panel has clear working space, is accessible, and is marked accordingly this shouldn't be an issue.
I was wondering if there was anything I might need to be concerned about code and non-code wise, but it seems like a completely plausible approach?
I informed them that the panels require a minimum of 3' clearance in front for maintenance, would prefer it the path was closed (not open grate) and that I would need to confirm with the structural team whether the weight of the panels and associated conduit could be properly supported. In response, they’ve proposed widening the mezzanine to 4' and passed the concern along to the Structural Engineer.
As far as I understand and have read in the NEC (240.24), as long as the Electrical Panel has clear working space, is accessible, and is marked accordingly this shouldn't be an issue.
I was wondering if there was anything I might need to be concerned about code and non-code wise, but it seems like a completely plausible approach?