MOV & Fuse Sequencing

Status
Not open for further replies.

BrianMuir

Member
Location
Comox BC
Hi,
I have a design involving a 69KV to 120V direct step down. We are protecting the primary with a pair of MOV arrestors and fuses.

I have drawn the MOV across the fuse and transformer primary, but the electrical contractor suggests the fuse should be ahead of the MOV.
See attached

mov.PNG


I don't think I agree with him but this isn't the kind of project I have a great deal of experience with and would welcome additional opinions.
thanks!
 
Utility company practice here is to indeed have the fuse ahead of the LA so if the arrestor fails (which it will eventually) the fuse will blow instead of creating a violent fault on the primary. But, that is ahead of a feeder with a fuse usually greater than 1 amp.

A call to your local power company's engineering department can provide you with the best answer.

Or, you could fuse the feeder right after the GOAB at say 25-100 amps, which will protect the LA's without nuisance blowing of the 1 amp fuse protecting your transformer. (As I can see a surge within the LA's capabilities easily blowing a 1 amp fuse.)

And for those who are wondering: :grin:

GOAB = Gang Operated Air Break (switch)
LA = Lightning Arrestor
 
ok, thanks for the excellent advice.
this all will be reviewed by the utility company but their policy is to "review rather than recommend".

The 1A fuse is a bit strange, I admit. The secondary load is something like 40A maximum, which on the primary equates to 70mA. This is why I have specified the smallest standard fuse rated at primary voltage. This said, I think we can increase the rating on that fuse if there is a benefit to doing so.
 