Firstly, I am not an EE or an electrician. I am the engineer (chemical) of an old industrial plant in NJ.
Our electrical switchgear is in a flood prone area and I am tasked to install new switchgear in a nearby higher elevation location.
The main power is a 2000A, 240V 3 phase, 3 wire delta-delta configuration. We bring power in at 4160V to three single phase distribution transformers on a pad.
The secondaries are wired to a three phase bus and then to 5 conduits containing 3 cables each. These cables are run through a wall and are then wired to the three phase bus in the electrical utilities’ cabinet; 5 cables per bus-bar.
Can anyone tell me why the wiring is configured this way? It seems like a lot of conductor material.
The 240V is used primarily to drive induction motors on agitators, vacuum pumps etc. The facility originally ran large resistive heating elements for their stills but thermal oil is used now. (The load on the 240 system does not rise above 800A.)
I am hiring an industrial electrical contractor to do the change but I would like to know something about the way things should be done prior to contracting.
Thanks
Tom
Our electrical switchgear is in a flood prone area and I am tasked to install new switchgear in a nearby higher elevation location.
The main power is a 2000A, 240V 3 phase, 3 wire delta-delta configuration. We bring power in at 4160V to three single phase distribution transformers on a pad.
The secondaries are wired to a three phase bus and then to 5 conduits containing 3 cables each. These cables are run through a wall and are then wired to the three phase bus in the electrical utilities’ cabinet; 5 cables per bus-bar.
Can anyone tell me why the wiring is configured this way? It seems like a lot of conductor material.
The 240V is used primarily to drive induction motors on agitators, vacuum pumps etc. The facility originally ran large resistive heating elements for their stills but thermal oil is used now. (The load on the 240 system does not rise above 800A.)
I am hiring an industrial electrical contractor to do the change but I would like to know something about the way things should be done prior to contracting.
Thanks