JimboSlice
New member
- Location
- Cambria, Ca, Usa
Hello. First post for me.
I have a question about a situation that is a little over my head as a service electrician. I recently was called to an imagining facility that does MRI scans. They had a MRI tech evaluate the system before they install a new MRI machine. In addition to loose connections in various switchgear and panels that i have already addressed, on of the issues he described is "the 300kVA transformer is maxed out. As you stand by it, outside, you can hear the transformer struggle with the loads-you can hear each pule of the MRI. Not normal. When new equipment is planned, ensure the power is upgraded to take into account new loads, and to provide some overhead for the transformer."
The transformer is a 300kva 3 phase 208/480 step up transformer, that feeds a 480v panel with 3 125 amp breakers, that feed the MRI machine, and 2 other pieces of equipment. I put a data logger on the primary side of the transformer, on the load side of a 600 amp breaker that is the primary OCD of the transformer. I just analyzed the data, and it doesn't appear to be near the capacity of the transformer. The maximum amperage on the primary side is between 350 and 420 amps on the various phases. at inrush peaks. the average amperage is more like 60-70 amps. My question is, is this a "normal" phenomenon, caused by collapsing magnetic fields? Does anyone have experience dealing with these machines? Also, the lights just outside the MRI room where the techs sit, dim significantly at certain high demand parts of the MRI process. however, these lights are on a "house" panel, not part of the switch gear that pertains to this office specifically. And I believe these are the only lights that dim...the ones close to the MRI room itself. Any insight from the super-geniuses would be great.
Thanks
I have a question about a situation that is a little over my head as a service electrician. I recently was called to an imagining facility that does MRI scans. They had a MRI tech evaluate the system before they install a new MRI machine. In addition to loose connections in various switchgear and panels that i have already addressed, on of the issues he described is "the 300kVA transformer is maxed out. As you stand by it, outside, you can hear the transformer struggle with the loads-you can hear each pule of the MRI. Not normal. When new equipment is planned, ensure the power is upgraded to take into account new loads, and to provide some overhead for the transformer."
The transformer is a 300kva 3 phase 208/480 step up transformer, that feeds a 480v panel with 3 125 amp breakers, that feed the MRI machine, and 2 other pieces of equipment. I put a data logger on the primary side of the transformer, on the load side of a 600 amp breaker that is the primary OCD of the transformer. I just analyzed the data, and it doesn't appear to be near the capacity of the transformer. The maximum amperage on the primary side is between 350 and 420 amps on the various phases. at inrush peaks. the average amperage is more like 60-70 amps. My question is, is this a "normal" phenomenon, caused by collapsing magnetic fields? Does anyone have experience dealing with these machines? Also, the lights just outside the MRI room where the techs sit, dim significantly at certain high demand parts of the MRI process. however, these lights are on a "house" panel, not part of the switch gear that pertains to this office specifically. And I believe these are the only lights that dim...the ones close to the MRI room itself. Any insight from the super-geniuses would be great.
Thanks