Has anyone installed or specified these filters in VFD applications?
http://www.mtecorp.com/products/dv-sentry-dvdt-filters/
I'd be interested to know what it is other than passive components.Has anyone installed or specified these filters in VFD applications?
Yes. I am also wondering makes it any different than a load side reactor with a better marketing brochure.I'd be interested to know what it is other than passive components.
Then just passive components.......It's a reactor + a capacitor and resistor making it an LRC low pass filter.
So what makes it a better type of sliced bread?
Pretty much what he said, although I don't have a hard rule about 50' and over (unless, as he said, it's a warranty requirement). Some drive mfrs have tested distances from drive to motor and I have found those to be reliable, so if the VFD mfr says you can go 400' from drive to motor, I don't add a filter to that one. But not all drive mfrs do that, so the 50' rule is a good plan if you don't know. On the other hand if someone has a 460V motor that was not built as "inverter duty" and is so special that it cannot be exchanged with a newer version (which is the case on some machine tools), I do it regardless of length.Yes I use the MTE DV/DT filter. I also use the TCI V1K. I mainly use them on submersible motors for pumps in wells. They are required for warranty purposes on any 460v 3 phase sub motor. They are recommended on 230v 3 phase motors but not required for the motor warranty.
most motors need a filter if they are more than 50 feet from the VFD. A simple line filter is usually acceptable up to about 300 feet. From 300 ft to 1200 feet you need a DV/DT filter, though for the small additional cost I use them for the under 300 ft application also. As Jraef mentioned, over 1200 ft distance you should be using a sine wave filter.
in 10 hp and under applications, I tend to use the TCI V1K. It's a little more expensive, but much more compact and quicker to install. I have discussed this with the MTE rep, and he's asked me to send a letter so that they can see what they can do about packaging the small filters in a more compact enclosure.