MTM switchgear

anbm

Senior Member
Location
TX
Occupation
Designer
When replacing the main, tie and feeder breakers (all draw out CBs) in MTM switchgear with new, same size & retrofitted CB, one CB at a time. Because these are draw out CBs, I assume the electrican wont need to shut down power to the switchgear for this task, correct?
 
When replacing the main, tie and feeder breakers (all draw out CBs) in MTM switchgear with new, same size & retrofitted CB, one CB at a time. Because these are draw out CBs, I assume the electrican wont need to shut down power to the switchgear for this task, correct?
One of the most risky things to do is to rack in/out breakers onto a live bus, especially with old or poorly maintained racking mechanisms.
 
Last edited:
Might not need a shutdown, but would then need one of those breaker-racking devices (e.g. https://safe-t-rack.com/) and some good PPE. Would also need a Plan B if something goes up the wall, like when a new breaker doesn't fully engage the bus.

Or, just schedule a shutdown for the replacement and get in all the other deferred maintenance at once :) . Planned shutdowns are often cheaper than a failure would be.
 
Top