I have read a number of threads here about sizing conductors for sub panels and have not found a definitive answer.
Here is a scenario that is common in the part of the world:
400 amp ces with 2 200 amp main breakers.
Panel is mounted on the exterior of an attached garage as per the PoCo.
Service is underground.
Ambient air temp in summer normally can reach 49c
The confusion starts when the (#2)main breaker feeds an existing 200 amp panel which currently is serving the living area.
The (#1) main breaker supplies the panel board which will feed various equipment in the garage, a well pump, swimming pool and a hot tub.
Table 310.15(B)(6) can be used to size 3-wire, single-phase, 120/240V service or feeder conductors that supply all loads that are part of or associated with the dwelling unit.
Using this table 3/0 cu thhn 90c would be the correct conductor as I interpret it.
Let the different views be heard.
Here is a scenario that is common in the part of the world:
400 amp ces with 2 200 amp main breakers.
Panel is mounted on the exterior of an attached garage as per the PoCo.
Service is underground.
Ambient air temp in summer normally can reach 49c
The confusion starts when the (#2)main breaker feeds an existing 200 amp panel which currently is serving the living area.
The (#1) main breaker supplies the panel board which will feed various equipment in the garage, a well pump, swimming pool and a hot tub.
Table 310.15(B)(6) can be used to size 3-wire, single-phase, 120/240V service or feeder conductors that supply all loads that are part of or associated with the dwelling unit.
Using this table 3/0 cu thhn 90c would be the correct conductor as I interpret it.
Let the different views be heard.