I agree.hmspe said:Which wire? The text in 310.15(B)(6) is specific on the requirements and on where the table can be used. If there is a single feeder to each unit you can use 31.16(B)(6) for that feeder.
I disagree, if the service is supplying more than one dwelling unit. A service disconnect for a 20-plex rated 400A (presumably one of many) could not use this table, IMO.If the service is 400A or less you can use the table for the service lateral.
310.15(B)(6): For individual dwelling units...
Brad, it would be most courteous to the original poster if you started a new thread for your question. But I will say that many jurisdictions require a engineer's stamp on one-lines and load calcs for such a large structure. I would recommend checking before spending much time on it.brad troxel said:I'm starting to do a 20unit condo complex (4000sqft ea) and haven't done one of these before. I'm thinking of doing maybe up to 3 service laterals (1 set) feeding a group of services which will me have the metering on them. My load calc will most likely be around the 2000A area. Any other ideas on the service layout.
Thanks,
Brad