I am studying for a contractors test and one of the questions has me stumped. Here it is
We have an 8 unit apartment complex, with a 120/208, 3 phase, 4 wire service. Each Apartment has a 4.5kw single phase 120/208 volt dryer. The question is what would be the minimum service demand be for these dryers. My calculations are below, but my answer is not one of the options.
8 / 3 = 2.6, round up to 3 then 3 * 2 = 6
8 - 6 = 2
5000 * 6 = 30,000 kva
5000 * 2 = 10,000 kva
40000kva * .6 (60%) = 24 kva But 24 is not an option
The options are 21, 27, 36 and 40 kw
charlie b
Lockport, IL
Semi-Retired Electrical Engineer
I get 18 KVA. You will have 3 dryers on A-B, 3 dryers on A-C, and 2 dryers on B-C. So the most between two phases is 3. The total load is therefore 5000 times (3x2), or 30 KVA. You reached this same point in your approach. I don't know why you are adding 10 KVA more. The code says that the total load is twice the load between any two phases. That is the 30 KVA. All that remains is to apply the 60% demand factor to the 30 KVA, and that is how I reached an answer of 18 KVA.
Now perhaps someone can tell me if my approach is flawed.
Dennis Alwon
Chapel Hill, NC
Retired Electrical Contractor
I agree with the 3 max per phase. 3 x 2= 6
6 dryer in Table 220.54 = 75%
6x 5000 = 3000 *.75 = 22500
22500 x 3/2= 33750kw
charlie b
Lockport, IL
Charlie I think you have to use 8 dryer and use 75%. I get 33,750kw
There is room for confusion here. My interpretation is that the total load could have been set at 8 times 5000. But it did not have to. We are allowed to count the total load as twice the load seen by the highest number of dryers connected between two phases. Balancing the load as best as possible puts no more than 3 dryers on any pair of phases. Twice that is 6, and 6 x 5000 is 30,000. So I will stick with that.
I did use the demand factor for 8 dryers. That is 60%, not 75%.
Smart $
Esteemed Member
Ohio
Look at the example D(5a) in the back of the book in annex D
That shows the calculation for ranges but the approach is nearly identical...
Dryers: Maximum number between any two phase legs = 3
3 per phase x 2 = 6 per leg
6@5,000VA ea. = 30,000VA
Table 220.54 demand = 30,000VA × 6@75% = 22,500VA
Per phase demand = 22,500 VA ÷ 2 = 11,250 VA
Equivalent 3-phase load = 3 legs @ 11,250 VA ea. = 33,750VA
The last two lines is where the 3/2 multiplier comes in.
Dennis Alwon
Chapel Hill, NC
Is that not the answer I had? I know it is for ranges but like you said it is the same calc.
Dennis Alwon
Chapel Hill, NC
The answer in my post—a slightly revised version of the Annex D Example—is exactly the same as your answer.
I gotcha. I just combined the division and multiplication to get 3/2- I guess I could have spelled it out but I figured if Charlie saw the example in the book he would see where it came from... Thanks
kwired
Electron manager
NE Nebraska
8 - 6 = 2
No one that has replied has come up with any of those answers, possible the person that wrote the question doesn't know the answer either?
Dennis Alwon
Chapel Hill, NC
My guess is they did exactly what Smart$ did only they used 60% instead of 75% (which is incorrect, IMO) and that comes to 27kw