reb707
New member
- Location
- Taylor Mill, KY
I am studying for a contractors test and one of the questions has me stumped. Here it is
We have an 8 unit apartment complex, with a 120/208, 3 phase, 4 wire service. Each Apartment has a 4.5kw single phase 120/208 volt dryer. The question is what would be the minimum service demand be for these dryers. My calculations are below, but my answer is not one of the options.
8 / 3 = 2.6, round up to 3 then 3 * 2 = 6
8 - 6 = 2
5000 * 6 = 30,000 kva
5000 * 2 = 10,000 kva
40000kva * .6 (60%) = 24 kva But 24 is not an option
The options are 21, 27, 36 and 40 kw
We have an 8 unit apartment complex, with a 120/208, 3 phase, 4 wire service. Each Apartment has a 4.5kw single phase 120/208 volt dryer. The question is what would be the minimum service demand be for these dryers. My calculations are below, but my answer is not one of the options.
8 / 3 = 2.6, round up to 3 then 3 * 2 = 6
8 - 6 = 2
5000 * 6 = 30,000 kva
5000 * 2 = 10,000 kva
40000kva * .6 (60%) = 24 kva But 24 is not an option
The options are 21, 27, 36 and 40 kw