Hi experts,
Recently, I received a machine from a manufacturer. The equipment itself is not UL certified and is imported from Asia. It is a multi-axis control machine that integrates up to 30 axis in one panel. The nameplate on the panel indicates FLA = 63A.
Upon closely examining the design, I found that there are 30 servo drives inside, each with an input current of approximately 5A.
Therefore, if I directly calculate the conductor for the feeder line of this panel, my understanding is 5A * 1.25 * 30 = 187A.
So for this panel, it should have a 200A breaker for feeder protection and 3/0 AWG wire for the feeder condutor inside the panel power distribution.
Currently, only a 3 AWG conductor and an 80A circuit breaker are used.
I inquired with the manufacturer, and they replied that due to the design logic, it is impossible for all servos to drive simultaneously. Moreover, each servo's actual load is below 50%, so they do not assess based on maximum full load.
In actual tests, I have never seen its full load current exceed 40A.
Due to space limitations in the panel, it is challenging for me to further increase the feeder conductor size and change a breaker for this panel...
Or a minumum change solution....
Section 430.26 provides guidelines regarding demand factors. Does this situation apply?
Recently, I received a machine from a manufacturer. The equipment itself is not UL certified and is imported from Asia. It is a multi-axis control machine that integrates up to 30 axis in one panel. The nameplate on the panel indicates FLA = 63A.
Upon closely examining the design, I found that there are 30 servo drives inside, each with an input current of approximately 5A.
Therefore, if I directly calculate the conductor for the feeder line of this panel, my understanding is 5A * 1.25 * 30 = 187A.
So for this panel, it should have a 200A breaker for feeder protection and 3/0 AWG wire for the feeder condutor inside the panel power distribution.
Currently, only a 3 AWG conductor and an 80A circuit breaker are used.
I inquired with the manufacturer, and they replied that due to the design logic, it is impossible for all servos to drive simultaneously. Moreover, each servo's actual load is below 50%, so they do not assess based on maximum full load.
In actual tests, I have never seen its full load current exceed 40A.
Due to space limitations in the panel, it is challenging for me to further increase the feeder conductor size and change a breaker for this panel...
Or a minumum change solution....
Section 430.26 provides guidelines regarding demand factors. Does this situation apply?