N ntegrity Member Nov 5, 2005 #1 I thought I seen somewhere in the code that required handle ties on breakers. I ran bk,r,bl,w x 2 with a ground to a J box and came out with 6 2wire mc cables I did not use handle ties on 6 single pole breakers is there any violation?
I thought I seen somewhere in the code that required handle ties on breakers. I ran bk,r,bl,w x 2 with a ground to a J box and came out with 6 2wire mc cables I did not use handle ties on 6 single pole breakers is there any violation?
George Stolz Moderator Staff member Location Windsor, CO NEC: 2023 Occupation Hospital Master Electrician Nov 5, 2005 #2 Re: multi ckts It's compliant so long as there are no receptacles served that have two circuits on the same yoke, and no line-to-line loads. See 210.4 and 210.7.
Re: multi ckts It's compliant so long as there are no receptacles served that have two circuits on the same yoke, and no line-to-line loads. See 210.4 and 210.7.