Multi-Conductor Cable Exiting Class 1 Div 1 Area
JustSomeGuy
New User
Minnesota
Controls Engineer
Hello,
I have an enclosure that is deemed a Class 1 Div 1 area and protected through intrinsically safe barriers. I have an RTD inside this enclosure to monitor temperature. I am using the manufacturer RTD cable between this area and the intrinsically safe barrier. I do not know if this cable is listed or not, if it is gas/vaportight, or if it transmits gas or vapors. I am currently waiting to hear back from the manufacturer with this information.
My question is, if the manufacturer tells me this cable is not listed, not gas/vaportight, and transmits gas or vapors, am I able to strip the jacket of the cable back past where the conduit sealing compound is and seal around the individual wires? Does this meet the requirements of 501.15(D)?
Additionally, if this cable is not listed, but I am using it per the manufacturers specifications, can I use it at all?
Howdy,
Many jurisdictions require cables to be listed, so whether you can use it in the first place would be up to the jurisdiction you are in. Additionally, stripping the cable jacket back and separating the wires for an extended run is probably not up to the manufacturer's specifications.