Re: Multi Conductor Cable
Even if it is allowed by the code, many industrial electricians and engineers make it a point to keep the 24 volt circuits separate from 120V to prevent problems with noise.
Imagine the capacitive and inductive coupling between the wires since they are bundled together so close. Its even worse if they run a long distance, worse for 480V than 120V, worse if the 480V is high current, and worse if the 24v circuits feed a high impedance (i.e. the input to a drive).
The result will be some unwanted noise on the input to the drive. Although the drive has probably been designed to reject a large amount of noise, if it does cause a problem, imagine how hard it would be to troubleshoot or fix later.
Steve