Re: multi-dewelling units calculation
The 1999 code had 100% for air conditioning in the same paragraph.
Please note, however, that this paragraph is for the ?Optional Calculation ? Dwelling Unit.? I?ve looked through the Section B calculation method. The only place it seems to explicitly mention air conditioning is to say that it can?t be part of the ?75% Demand Factor for 4 or more fixed appliances? given in 220-17.
I think it is possible (whether correctly or incorrectly) to assign a 125% factor for air conditioning via the following path: Start with 220-14, ?Motors.? It says that motor loads shall be computed per 430-24, -25, or -26. Next go to 430-24. It says that the conductor feeding several motors (or one motor with other loads) must have an ampacity based on 125% of the largest motor on the circuit (plus 100% of the other loads). But that relates to the ampacity of the cable, not to the amount of load to be included in the service or feeder calculation. So do you use 100% or 125%? 430-24 does not answer this question.
In the 2003 code, the wording of the 1999 Section 220-14 has been moved to 220.3(B)(3). It points the reader to 440.6 for air conditioning loads. In 440.6, there is no requirement to use a 125% factor.