Grouch
- New York, NY
If you design / install a solar PV system for an apartment building with multiple apartments, say for example 25 apartments, and there's base building areas such as lobbies, corridors, cellar with all the back-of-house areas... I have the following questions (each with my answer in red, if you can please correct where needed):
1. Can the output of the inverter be connected to the line side of the service switchboard (which is allowed by the 2008 section 690.64(A)), thereby providing power to the whole building (apartments, base building areas, etc.)? My answer is yes.
2. Can the output of the inverter be connected to the line side of the house distribution panel (at the feeder coming into the panel), thereby providing power to only the base building areas? My answer is no, because it has to be connected via a dedicated circuit breaker or fusible disconnecting means once you are on the load side of the service disconnecting means, based on 690.64(B).
3. Can the output of the inverter be connected to a dedicated circuit breaker or fusible disconnecting means on the house distribution panel, thereby providing power to only the base building areas? My answer is yes.
4. Are you free to choose either 1 or 3? My answer is yes, dependent on the size / KW rating of the array.