When we did our dwelling unit feeder calculations, we included EV Chargers among the "...appliances that are fastened in place, permanently connected, or located to be on a specific circuit" [220.82(B)(3).a.], which makes it part of the 1st 10 kVA plus 40% of the rest. The overall service calculation includes them under the diversities of Table 220.84.
A plan reviewer is telling us we may not apply either of these diversity factors to the EV Chargers. Am I missing something in The Code?
A plan reviewer is telling us we may not apply either of these diversity factors to the EV Chargers. Am I missing something in The Code?