Multi Family dwelling (condo's) bonding question
Mes,AZ
Just picked up some condos in Mesa,AZ. Havnt done multi family before, each building is three story with 12 units in each, four per floor, multiple garage units.They're set up like an apartment complex.
800amp service on the dwelling, three meter packs with four meters in each along with a 200amp house panel for parking lot lights, lollipops etc... and a 200amp on the garage which will be servicing multiple garages
1st question:
Each garage has a fire riser, does each one have to had a bond wire to and would it have to go back to the 200amp main on the garage for each riser in the garage? Only the garage with the 200amp main will have a loadcenter, the other garages will have fuseable discos.
2nd question:
For the fire riser in the dwelling, can that go in the 200amp house panel? Or does that have to go back to the actual SES, the 800amp:??
Have you read 250.104? There are several options on where to connect your bonding conductor... but generally speaking, it gets connected to the local GES.