does the ground (uffer) and nuetral (grounded conductor)need to be bonded together inside the SES? It has a spot in the SES to bond them but I can't remeber if it needs to be bonded
If SES=Service Disconnecting Means (SDM), the actual NEC term, it's as Gus pointed out. What is required at the SDM(s) is a Main Bonding Jumper (MBJ) between Grounded conductor and Equipment Grounding System. If a GEC terminates in an SDM, it can be connected at either end of the MBJ, to the Grounded Conductor or the Equipment Grounding System.does the ground (uffer) and nuetral (grounded conductor)need to be bonded together inside the SES? It has a spot in the SES to bond them but I can't remeber if it needs to be bonded