Hello Everyone.
I have used 220.84 many times in the past however I have only applied it to a single meter center.
My situation is this. I have one Main MDP feeding 8 meter centers. Each of the meter centers is feeding approximately 8 dwelling units. I just want to make sure it is permissable to use 220.84 once on the individual meter centers, and then re-apply the demand factor to the MDP.
Hypothetical Example:
Each dwelling unit has a connected load of 24kW.
Meter center Main. 24kW * 8 Units = 192,000 * 0.43 (220.84) = 82,600 @ 208-3 is 229 Amps. I would use a 400A.
MDP Sizing: 192,000 * 8 meter centers = 1,536,000 * 0.23 (220.84) = 353,280 total watts @ 208-3 is 982A. I would use a 1000A breaker with this.
Does this sound correct?
PS> If you wondering why I am using 208-3 instead of 208-1 its because the meter centers are 3phase in and single phase out.
Thanks!!!!
I have used 220.84 many times in the past however I have only applied it to a single meter center.
My situation is this. I have one Main MDP feeding 8 meter centers. Each of the meter centers is feeding approximately 8 dwelling units. I just want to make sure it is permissable to use 220.84 once on the individual meter centers, and then re-apply the demand factor to the MDP.
Hypothetical Example:
Each dwelling unit has a connected load of 24kW.
Meter center Main. 24kW * 8 Units = 192,000 * 0.43 (220.84) = 82,600 @ 208-3 is 229 Amps. I would use a 400A.
MDP Sizing: 192,000 * 8 meter centers = 1,536,000 * 0.23 (220.84) = 353,280 total watts @ 208-3 is 982A. I would use a 1000A breaker with this.
Does this sound correct?
PS> If you wondering why I am using 208-3 instead of 208-1 its because the meter centers are 3phase in and single phase out.
Thanks!!!!