Re: multi family service calculation
Just to make sure I understand your question, what I read is that the engineer used 220.30, ?Optional Calculation ? Dwelling Unit,? for the feeder to each apartment, and then used 220.32, ?Optional Calculation ? Multifamily Dwelling,? for the building service. If that is your question, my answer is ?yes, this is acceptable.? The engineer is not mixing calculation types.
But the engineer could mix calculation types, if that served to the owner?s advantage. For example, it is acceptable to use the standard calculation method for each unit, and the optional method for the building as a whole.
But keep in mind that each calculation must be done separately, and in accordance with the rules for that type of calculation. For example, suppose that the engineer used the optional method, including its demand factors, for each unit. Suppose further that the engineer added up the calculated results, and did not, as you described, add up the connected loads of all units. Suppose finally that the engineer then applied the multi-family demand factors to the total building loads. This method would be invalid, for it would apply the building?s demand factors on top of the individual unit?s demand factors. We don?t get to ?double-dip? in this way.
Does this answer your question?