I have 63 units at 208V.
my connected load is 1650KVA.
my total calculated load (with demand factor of 23% 220.84) is 380KVA.
My service conductors need to be rated for 1055A.
Do i need to multiply this by 125% to get my OCPD (1600A)? Or just round up to 1200A??
Thanks! (code sections would be great)
my connected load is 1650KVA.
my total calculated load (with demand factor of 23% 220.84) is 380KVA.
My service conductors need to be rated for 1055A.
Do i need to multiply this by 125% to get my OCPD (1600A)? Or just round up to 1200A??
Thanks! (code sections would be great)