multi family service

Status
Not open for further replies.

tower

Member
Location
Massachusetts
in a multi family service, can I use table 310.15(b)(6).for the main service.and all so for sizing the feeders to the apartments service panels.
 
Re: multi family service

In my opinion, if the main panel does not contain breakers other than for the feeders, you could use 310.15(B)(6).

If you have other OCPD's in the "main" panel, you would have to use 310.16
 