rikcoop
Member
- Location
- Sacramento, CA
I have a plan reviewer stating the unit mains & Building Main needs to be 100% rated. Unit load calculations were done per 220.82 (98.28 Amps), and I used the optional calc for the Building Load 220.84. (1157.05 Amp)
I have 100 Amp mains for units, and 1200 Amp main for the building.
Being that residential loads are non-continuous, I don't agree the mains should be required to be 100% rated.
Any suggestions on code reference to support my opinion?
I have 100 Amp mains for units, and 1200 Amp main for the building.
Being that residential loads are non-continuous, I don't agree the mains should be required to be 100% rated.
Any suggestions on code reference to support my opinion?