mkgrady
Senior Member
- Location
- Massachusetts
I don't usually work in the city (Boston) so I'm not up on how to deal with a multi meter situation. A 14 unit apartment building has a 200 amp, 120/240v service. The main feeds 15 meters and breakers that feed student apartments upstairs. The only exception being one of the 15 meters feeds a house panel with a 40 amp main. This panel is clearly overloaded with about 16-1 pole 20's and a 2-pole 30, and needs to be upgraded. I can't tell what all these house circuits feed but the normal load must have been below 40 amps because it never tripped until recently (so I'm told). The reason I'm there is because a heating contractor installed a new oil burner that requires a 30 amp 230 volt circuit for a 3hp burner motor. They reused the existing 2-pole 30 cb in the house panel. Two things are happening. The 40 amp main on the house panel is tripping occasionally (no surprise but I don't know why it wasn't tripping on the old heat system) and the oil burner 3hp motor has failed twice in two weeks. The heating contractor has asked me to upgrade the house panel to 100 amps because he feels the new oil burner motor is failing because of a low voltage condition due to the inadequate house panel feed. I don't know if upgrading the panel to 100 amp will correct the failing motor problem but it seems necesssary regardless. So now finally to my question. Can I connect a 100 amp panel to the existing meter? How do I find out? My first thought was to look inside the meter socket to see if it will accept 100 amp wire. Sorry for such a long post.