Just hope for someone to look over my numbers and see if I am on the right page.

Control Panel with
(1) 50 HP Motor 65A FLA @ 480
(8) 1 HP Motors 2.1A FLA @ 480

Feeder size Based on NEC 430.24
(65A * 1.25) + (2.1 * 8) = 98A Minimum (Select #3 THHN)

Breaker Overcurrent Protection Based on NEC 430.62
(65A * 2.5) + (2.1 * 8) = 179A Maximum (Select 150A Breaker)

Ground based on 150A Breaker and NEC 250.122
#6

I just want to clarify that this is not considered a tap and the NEC doesn't have any distance limitations on the feeder length.

Thanks Ahead of Time,

Steve
 

david luchini

Moderator
Staff member
Location
Connecticut
Occupation
Engineer
Just hope for someone to look over my numbers and see if I am on the right page.

Control Panel with
(1) 50 HP Motor 65A FLA @ 480
(8) 1 HP Motors 2.1A FLA @ 480

Feeder size Based on NEC 430.24
(65A * 1.25) + (2.1 * 8) = 98A Minimum (Select #3 THHN)

I'd say this is correct.

Breaker Overcurrent Protection Based on NEC 430.62
(65A * 2.5) + (2.1 * 8) = 179A Maximum (Select 150A Breaker)

150A is acceptable, but it is not the maximum permitted per 430.62, 175A is the maximum permitted.

The calculation would actually be 65A * 2.5 = 162.5 => 175A (next size up per 430.52.)

175 + (2.1 * 8) = 191.8A Maximum, which would be a 175A c/b.

Ground based on 150A Breaker and NEC 250.122
#6

I just want to clarify that this is not considered a tap and the NEC doesn't have any distance limitations on the feeder length.

Thanks Ahead of Time,

Steve

#6 ground would also be OK for a 175A c/b. This is not a tap and there is not length limitation on the feeder. Each of the motors would need a branch circuit OCPD in accordancee with 430.52.

(The "control panel" may actually full under Article 409, but I think the conductor and OCPD sizing would be the same.)
 
Last edited:

StephenSDH

Senior Member
Location
Allentown, PA
I see you can use a 175A breaker. I leaned down to 150A because on my square d slide chart they show a using a 100A (FAL34100) breaker for a 50HP motor which is only FLA x 1.5. I guess it has the do the the instantanious trip of that breaker that they don't use the full 2.5. I don't believe all the motors will be be running at the same time, so I didn't want to oversize too much more then I need. I am not installing the feeder or selecting the breaker so I don't know what breaker type they will choose.

I do have individual overcurrent protection for each motor.

Thanks, Steve
 