teco
Senior Member
- Location
- Mass north shore
Hello, Can anyone help with this? I have a roof unit to be wired and it has been a custom built unit for the customers needs. There is five pieces of equipment built in to one unit by the factory. All have motor load of fans,compressors, etc. The factory nameplate total calls for and f.l.a. of 82.2 amps and an mca of 97 amp and an mop of 110 amps. I believe the 97 includes 125% of the largest motor. The unit runs all day. I believe I need to apply 125% for continuous load to the 97 amps which brings it to 121.25 amps. Also adding a 200 amp disconnect to keep an mop of 110 amps. The hvac contractor says this requires only a 100 amp feed. I don't agree. Any opinions would be great.
Thanks.
Thanks.