Having a debate with myself. When calculating a service disconnect with multiple motors and other loads, the calc is based on the largest motor FLC x 1.25% + remining motor FLC + other loads (1.25% if continuous). However, this can result in a smaller main than a feeder OCPD with multiple motors, so which is correct?
Here is an example: Enclosed breaker or fused service disconnect feeds an ATS which feeds a panel with main breaker and individual branch breakers for 3 motors at 20HP 208V 3-phase each and 10A 3 phase other non-continuous load.
Service calc: (62.1FLC x 1.25%) + 62.1 + 62.1 + 10 = 211.8A so 225A service disconnect breaker or fuse size.
Feeder OCPD calc: 62.1 FLC x 2.5 = 155.25A = 175A breaker + 62.1 + 62.1 + 10A= 309.2A = 350A.
So should the service be at 225A and the panel main breaker be at 350A per code? The reason a I suspect a motor feeder OCPD is large is due to the motor inrush to insure the OCPD does not trip when motors start. However, this would carry through to the service disconnect as well so why should it not be sized in the same manner? Shouldn't the entire system and service be rated for 350A? What if the service went right to the panel and the panel main was the service disconnect? It only needs to be 225A correct?
Here is an example: Enclosed breaker or fused service disconnect feeds an ATS which feeds a panel with main breaker and individual branch breakers for 3 motors at 20HP 208V 3-phase each and 10A 3 phase other non-continuous load.
Service calc: (62.1FLC x 1.25%) + 62.1 + 62.1 + 10 = 211.8A so 225A service disconnect breaker or fuse size.
Feeder OCPD calc: 62.1 FLC x 2.5 = 155.25A = 175A breaker + 62.1 + 62.1 + 10A= 309.2A = 350A.
So should the service be at 225A and the panel main breaker be at 350A per code? The reason a I suspect a motor feeder OCPD is large is due to the motor inrush to insure the OCPD does not trip when motors start. However, this would carry through to the service disconnect as well so why should it not be sized in the same manner? Shouldn't the entire system and service be rated for 350A? What if the service went right to the panel and the panel main was the service disconnect? It only needs to be 225A correct?