- I would appreciate your help with a energy reduction program being implemented by Wal-Mart Stores Inc. Proto Design Engineering Department and the Technical Service Departments. Vendors, suppliers, manufactures and third party consultants are providing Wal-Mart information from their prospective and are conflicting. I'm looking for a non-biased opinion on what would be the correct business decision.
Subject: Retrofitting existing refrigeration condensing units with VFD drives to regulate air flow. Ambient operations control, Delta T control across condenser, compressor discharge pressure control, and most important energy savings for the entire refrigeration system. A single VFD drive controls the RPM for anywhere from 4 to 10 condenser fan motors.
Existing motors are installed on a refrigeration medium and low temperature application air cooled condensers. The condensers have anywhere from 4 to 10 motors being staged using individual contactors for each motor. The condenser fan motor contactors are being controlled by a Energy Management System.
Presently we are installing the VFD drives on condensers equipped with 3 phase 460 volt 575, 850, 1140 RPM non-rated VFD motors equipped with internal thermal overloads. NOTE: the VFD drives are equipped with a LC filter to eliminate any spike voltages that could be developed in the feeder to the motors. The existing wiring is single conductor #14 THWN str.wire installed in a C channel bundled together. The wiring varies in length from 8ft - 35ft depending on the motor location within the condensing unit deck plate. If any existing motors fail we are replacing them with VFD rated condenser fan motors equipped with shielded cabling, externally wired thermal protection interconnected with a starter assembly. The external wired motor thermal overload and the started current sensing overload are wired in series with the starter coil control circuit. The starter assembly current overload is set for manual reset.
QUESTION: Replacing existing 3 phase 460 volt 575, 850, 1140 RPM non-rated VFD motors equipped with internal thermal overloads refrigeration condenser motors with equivalent specification high efficiency VFD rated motors with externally wired thermal overloads when the VFD drives are installed the correct decision?
1/2 HP, 575 RPM, CONDENSER MOTOR, W/ BASE
1 HP, 850 RPM, CONDENSER MOTOR, W/ BASE
3/4 - 1 HP, 850 RPM, CONDENSER MOTOR, W/O BASE
1-1/2 HP, 850 RPM, CONDENSER MOTOR, W/ BASE
1-1/2 HP, 850 RPM, CONDENSER MOTOR, W/O BASE
1-1/2 HP, 1140 RPM, CONDENSER MOTOR, W/ BASE
1-1/2 HP, 1140 RPM, CONDENSER MOTOR, W/O BASE
Here are my thoughts
Multi-motor applications on a single drive typically requires motor thermal overloads to be externally wired. Typically, a internal motor thermal overload doesn't always disconnect all three legs simultaneously. VFD drives need a balanced load to work properly.
The LC filter wouldn't be needed if we used VFD rated electric motors feed with shielded cable.
VFD rated motors are better equipped to handle the low air flow conditions associated with VFD applications
Wal-Mart is cost driven and a return on investment must exist to drive this decision (Safety and Reliability are a given)
The replacement of sunlight/exposed THWN with rated cable will reduce maintenance
Other questions
If we eliminate the LC filter on the drive then the shielded cable will need to be rated for what voltage? Presently the cable we are using is rated for 600 volts. The drain leg on the shielded cable is wired to the condenser frame and in connected with the equipment ground terminal lug.
Thank you,
vincecharles
Subject: Retrofitting existing refrigeration condensing units with VFD drives to regulate air flow. Ambient operations control, Delta T control across condenser, compressor discharge pressure control, and most important energy savings for the entire refrigeration system. A single VFD drive controls the RPM for anywhere from 4 to 10 condenser fan motors.
Existing motors are installed on a refrigeration medium and low temperature application air cooled condensers. The condensers have anywhere from 4 to 10 motors being staged using individual contactors for each motor. The condenser fan motor contactors are being controlled by a Energy Management System.
Presently we are installing the VFD drives on condensers equipped with 3 phase 460 volt 575, 850, 1140 RPM non-rated VFD motors equipped with internal thermal overloads. NOTE: the VFD drives are equipped with a LC filter to eliminate any spike voltages that could be developed in the feeder to the motors. The existing wiring is single conductor #14 THWN str.wire installed in a C channel bundled together. The wiring varies in length from 8ft - 35ft depending on the motor location within the condensing unit deck plate. If any existing motors fail we are replacing them with VFD rated condenser fan motors equipped with shielded cabling, externally wired thermal protection interconnected with a starter assembly. The external wired motor thermal overload and the started current sensing overload are wired in series with the starter coil control circuit. The starter assembly current overload is set for manual reset.
QUESTION: Replacing existing 3 phase 460 volt 575, 850, 1140 RPM non-rated VFD motors equipped with internal thermal overloads refrigeration condenser motors with equivalent specification high efficiency VFD rated motors with externally wired thermal overloads when the VFD drives are installed the correct decision?
1/2 HP, 575 RPM, CONDENSER MOTOR, W/ BASE
1 HP, 850 RPM, CONDENSER MOTOR, W/ BASE
3/4 - 1 HP, 850 RPM, CONDENSER MOTOR, W/O BASE
1-1/2 HP, 850 RPM, CONDENSER MOTOR, W/ BASE
1-1/2 HP, 850 RPM, CONDENSER MOTOR, W/O BASE
1-1/2 HP, 1140 RPM, CONDENSER MOTOR, W/ BASE
1-1/2 HP, 1140 RPM, CONDENSER MOTOR, W/O BASE
Here are my thoughts
Multi-motor applications on a single drive typically requires motor thermal overloads to be externally wired. Typically, a internal motor thermal overload doesn't always disconnect all three legs simultaneously. VFD drives need a balanced load to work properly.
The LC filter wouldn't be needed if we used VFD rated electric motors feed with shielded cable.
VFD rated motors are better equipped to handle the low air flow conditions associated with VFD applications
Wal-Mart is cost driven and a return on investment must exist to drive this decision (Safety and Reliability are a given)
The replacement of sunlight/exposed THWN with rated cable will reduce maintenance
Other questions
If we eliminate the LC filter on the drive then the shielded cable will need to be rated for what voltage? Presently the cable we are using is rated for 600 volts. The drain leg on the shielded cable is wired to the condenser frame and in connected with the equipment ground terminal lug.
Thank you,
vincecharles